seasick said:
JeffN said:
. The mention of continuous loads (a constant load for three hours or more) above is for sizing circuits for fixed equipment and is allowed for at the design and installation phase and not for a general use circuit - the breaker does not know if the load is continuous or not. If it is a 20 amp breaker it will supply 20 amps.
quote]
This is not true. Breakers use bi-metal thermal mechanisms that actually heat up with the load. The more the load, the more they heat up and at some point the bi-metal strip bends enough to trip the breaker. You can pull a lot more amperage than 20 amps through a 20 amp breaker as long as it is for a short period of time. Generally breakers will carry 80% of rating forever. 110% may work for 5 minutes or an hour depending on the design and intended use.
For example, a large compressor type load could spike several times its continuous draw but you would size for the smaller draw and not the start up peak current.
One other factor to consider is voltage drop. Even with properly designed distribution, there is a designed voltage drop figured in the wire sizing. When you have long service runs, add extension cords etc., you may add more resistance and under load more voltage drop. For resistive loads like lights, that results in dimmer lighting, no big deal, but for constant load devices like compressors, low voltage due to drop results in higher current. That can lead to breaker trips at best and burned out motor windings at worst.
A lot of DIYers assume that for a 20 amp service you need a 12 gauge wire but that it true up to a length limit(about 50 feet). It is not uncommon to see undersized wires for longish runs. Note that a 12G extension cord is a hefty cable. A 10 G is really bulky. Your run of the mill extension cords are usually sized much smaller
Circuit breakers have a time delay function to allow for spikes of starting current etc. I would direct you to NEC aticle 100-I for a definition of continous load. Then go to article 210-19 (A) and 210-20 (A), in the 2008 Nec, for more info about sizing a circuit for continuous loads. These factors are used for sizing continuous loads that are fixed/known loads. Who knows at the time of construction what equipment a boat will have that happens to tie up in that slip? How will you size for a continuous load on a receptacle when you don't know what willl be plugged into said receptacle. In addition there is an entire section in the NEC, article 430, for motors like for the compressors you mention above. In a motor application the the over current protection is permitted to be increased to allow for current surges. This information is available in table 430.52 again in the 2008 NEC my 2011 book is out in the van currently. The breaker can be oversized because the motor is protected by the heaters in the motor or motor controller. In the case of a single phase motor an inverse time circuit breaker can be increased 250% after you have done your motor calculations. Thats why you will see 12 gauge conductors on a motor feed protected by a breaker larger than 20 amps. You can't just throw a larger circuit breaker on a circuit with a unknown load, like on at a dock. The dock receptacle the OP mentions I would guess is sized for either 15 or 20 amps, perhaps 30 amps and the conductors are matched to that overcurrent device. If it is protected and sized for a 20 amp overcurrent device he will have 20 amps available. The 16 amps (or 80% of 20 amps) you mention is part of a continuous load calculation that no one is able to complete as the receptacle does not have a fixed known load.
Voltage drop, conductor size and other factors are all part of the calculation of course but there is more to it than that.